Hi @cavassiGE, Thank you for your questions. Here is my attempt to answer them:
Yes, you should add a load (resp. generator) at every location where you expect an energy consumer (resp. producer) - i.e., the same locations in which you would have a load if you were to run a power flow calculation. In your case, if my assumption is correct, that that would be at the red nodes. However, you do not need to assign The rest of your setup seems to be OK. I hope this helps. Please let us know how it goes! |
Beta Was this translation helpful? Give feedback.
-
|
Thank you for your answer! You are correct, the red nodes are where the voltage and active/reactive power is being measured. So having the loads here makes sense. I have now added the sym_load components, which naturally changed the output. But the results are still not looking very good. The error tolerance need to be minimum 2e-1 for the estimation to be able to run, which I believe is way higher than wanted. To give you as much context as possible, I'll share the file where I create the PowerGridModel object, as well as the config which is now slightly updated. I have tried tweaking some of the constants, but I'm afraid my physics knowledge are not good enough to know what a reasonable value is for most of them. I'll also share the results, but since the data used as input is classified, I've had to round/remove/modify some of the output values. But the overall picture is still the same. Not sure if these points are interesting, but some things to notice are:
I've added some TODOs in the code for things that I'm not sure about. Thank you again! |
Beta Was this translation helpful? Give feedback.
-
|
Changing the
using p.u gave me a Max deviation of 110
I tried doing the ID changes without reverting from 1. and got that there were Then I also tried changing the ID's with all the voltage sensors. with both p.u values and Volt. Volt gave me a max deviation of 1.7 |
Beta Was this translation helpful? Give feedback.

Hi @cavassiGE,
Thank you for your questions. Here is my attempt to answer them:
Yes, you should add a load (resp. generator) at every location where you expect an energy consumer (resp. producer) - i.e., the same locations in which you would have a load if you were to run a power flow calculation. In your case, if my assumption is correct, that that would be at the red nodes.
However, you do not need to assign
p_specifiedandq_specified, as the power consumption will be calculated from the sensor measurements. The reason you need to specify the loads is so that the Power Grid Model knows wher…